I recently purchased a 1971 mobile home with a 60 amp circuit breaker service. I would like to install a 100 amp circuit breaker panel before having the power turned on. I have changed panels before, fuse to circuit breaker, but they were the same amperage. Is this okay to do and should I alert the power company before having power tuned on?

Spork

  • Walrus Stache
  • *******
  • Posts: 5742
    • Spork In The Eye
Re: electric panel upgrade from 60 amp to 100 amp
« Reply #1 on: May 19, 2017, 07:47:12 AM »
I am NOT an electrician.  But I would absolutely talk to the power company.

You could probably ballpark it by looking at the size of the wire incoming and going to the googles... but I'd still call. 

Does your power terminate at the mobile home?  Or does it terminate on a pole outside with a wire running to an interior panel?  If it is the former, you're likely to need to re-run the pole-to-panel run yourself.  (I've normally seen mobile homes with a meter on a pole next to the home instead of bolted straight to the house.)

And if I were going to that much trouble.... I might go ahead and upgrade to 200amp.

ncornilsen

  • Handlebar Stache
  • *****
  • Posts: 1047
Re: electric panel upgrade from 60 amp to 100 amp
« Reply #2 on: May 19, 2017, 09:55:29 AM »
Confirm the size of the conductors feeding this panel are rated for 100 amps.

does this mobile have aluminum wire? If so... well, google how to deal with that.

paddedhat

  • Handlebar Stache
  • *****
  • Posts: 2228
Re: electric panel upgrade from 60 amp to 100 amp
« Reply #3 on: May 19, 2017, 04:50:34 PM »
Lots of issues here. If I imagine running into this situation in my local area, these are the issues I would probably encounter. OTOH, you might have the same, or totally different issues completing this work.

  First, the service wire from the panel to the meter and the meter to the utility connection point is not large enough to support a 100 service. Second when you upgrade that wire you will need a new meter base that is approved by the utility for their meter. If he service is on a stand alone pole that is part of the "customer side" of the service, it may, or may not suit current codes. I've seen poles that are too short to allow the utility to install their wire at a safe height and multiple poles that rotted and fell over.  Next you will have to install additional grounding at the service, including two ground rods, and the proper ground wire. Next the installation needs to be inspected by a licensed inspector who will issue a "cut-in" card which will allow the utility to connect the power. This inspector will want to do a general inspection of the homes system to look for aluminum Romex, grounded outlets, GFCI protection in kitchen and baths. As a result, a significant amount of upgrading to the electrical system inside the trailer may be required.

Not to be the bearer of bad news, but these jobs, in many heavily inspected areas, can turn into a real cluster F. In other areas, they can be cheap and easy, if there is no real need to get inspectors involved. My local utility requires that everything get inspected before they reconnect, so there is no way to work around the issue. Good luck.

 